Our full technical support staff does not monitor this forum. If you need assistance from a member of our staff, please submit your question from the Ask a Question page.


Log in or register to post/reply in the forum.

Documentation of Delay() instruction


Anton Jan 15, 2024 01:47 PM

The documentation of the delay() instruction is somewhat confusing to me.  See here for example:

https://help.campbellsci.com/crbasic/cr6/#Instructions/delay3.htm#kanchor386

It says "For the Delay instruction, the Option parameter determines whether the delay should apply to the measurement task sequence or the processing instructions."  This is consistent with the choices see in the CRBASIC editor.

But the table in the help and the text in the remarks section suggest that both options apply delays to measurement and processing.

Am I misreading something?


JDavis Jan 15, 2024 11:30 PM

Thanks for pointing this out. It appears information from the CR300 help was incorrectly applied to the CR6 and CR1000X help.

The choices in the editor are correct.

I will report this to get the help corrected.

Log in or register to post/reply in the forum.