christophe Apr 7, 2016 08:43 AM
hello, is it possible to record  CR1000 data only between 8:00 am and 8:00 pm ?
Thanks
Chris

JDavis Apr 7, 2016 03:39 PM

The DataTable instruction has a TrigVar parameter that effectively turns the table on and off. A simple solution would be to use the TimeIsBetween instruction to set the TrigVar parameter.


christophe Apr 8, 2016 08:20 AM

thanks for your anwer

 i try this solution in my program but it doesn't work .... nothing at 10h00am ... what's wrong ?

StationName (05_PH2016_SRS)

SequentialMode
BeginProg
  If TimeIsBetween (10,17,24,Hr)Then
    Scan (5,Sec,0,0)
        PanelTemp (PTemp,250)
        Battery (batt_volt)
        
        'Apply power to white wire of both sensors through SW-12
        PortSet (9,1)
        'Delay for at least 250 mSec for sensors to enter SDI-12 mode.
        Delay (0,1,Sec)
        'Query sensor for 3 SDI-12 outputs.  Default address for all Decagon Digital sensors is 0.
        SDI12Recorder (UpOut(),1,0,"M!",1.0,0)
        SDI12Recorder (DownOut_Pur(),3,0,"M!",1.0,0)
        SDI12Recorder (DownOut_Mel(),5,0,"M!",1.0,0)
        'Turn SW12V off
        PortSet (9,0)
        'calculate NDVI from individual outputs of both sensors.  See equation 1 of the SRS manual
        NDVI_Pur = (DownNIR_Pur/UpNIR - DownRed_Pur/UpRed)/(DownNIR_Pur/UpNIR + DownRed_Pur/UpRed)
        NDVI_Mel = (DownNIR_Mel/UpNIR - DownRed_Mel/UpRed)/(DownNIR_Mel/UpNIR + DownRed_Mel/UpRed)
      
        
        'Call Output Tables
        CallTable NDVIdata
    NextScan
    Else
      PortSet (9,0)
    EndIf
EndProg

thanks


Dana Apr 8, 2016 06:53 PM

Move your "TimeIsBetween" after Scan. As it sits now, TimeIsBetween is only evaluated once, at compile time, and is never checked again.

Dana W.


JDavis Apr 8, 2016 10:07 PM

I would use the TimeIsBetween in the DataTable instruction in the TrigVar parameter. You do not need an If statement.

Public PTemp, batt_volt


DataTable (Test,TimeIsBetween (10,17,24,Hr),9999) 'Set table size to # of records, or -1 to autoallocate.
DataInterval (0,15,Sec,10)
Minimum (1,batt_volt,FP2,False,False)
Sample (1,PTemp,FP2)
EndTable

'Main Program
BeginProg
Scan (1,Sec,0,0)
PanelTemp (PTemp,250)
Battery (batt_volt)

CallTable Test
NextScan
EndProg


christophe Apr 18, 2016 01:32 PM

ok Thanks ..