Panel temperature measurement returns NAN


smeck Aug 19, 2016 11:00 AM

Hello,

this instruction in our program for CR1000 was working very well:

PanelTemp(PanelTemper,_50Hz)

Suddenly (no touch of software, hardware, ...) it started returning NAN.

Is there anything what I can try to change or is it problem of internal connection of temperature sensor inside of the datalogger?

thanks

Smeck


aps Aug 19, 2016 12:56 PM

It could be a internal fault but more likely you have a voltage of >7 Volts connected to one of the analogue inputs on the wiring panel which in turn is upsetting the logger.   This is not an uncommon fault.


smeck Aug 24, 2016 10:36 AM

Hello aps,
thanks for your tip. We have some voltage dividers in station and probably it was something of this kind, becouse after checking and tightening of all terminal connections, NAN disappeared.
thank you
Smeck 